I have never had to do this but why can't you leave the gec's as they are and just add another ground rod from the first rod
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I'm curious how the OP connected the conductors from the 3 200 amp mains to the meter socket. I've only seen 320 meters accept 2 conductors.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I'm curious how the OP connected the conductors from the 3 200 amp mains to the meter socket. I've only seen 320 meters accept 2 conductors.


That is a 600 amp meter base. The panel on the far right is feed out the back and there are 3 conductor lugs for it. There are CT's in the meterbase
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You can see the pics in this thread. I did have to change the lugs to 3 conductor lugs. I had to order it thru the power company as the supply companies could get them. They gave me the lugs

 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
You can see the pics in this thread. I did have to change the lugs to 3 conductor lugs. I had to order it thru the power company as the supply companies could get them. They gave me the lugs

I’ve got boxes of two hole and three hole spades we used to give away to electricians. Haven’t had anyone ask for them in a couple of years..
Think I may even have a few four hole spades.
D81218A4-A39D-4565-B103-A0BABBD6223A.jpeg
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I’ve got boxes of two hole and three hole spades we used to give away to electricians. Haven’t had anyone ask for them in a couple of years..
Think I may even have a few four hole spades.
View attachment 2558540


Put them online I bet you can get a good price for them. I don't think I ever bought more than a couple of double lugs in my life.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
He also said that I needed 2ea grounding rods (one on each end of the meter rack) instead of just one. I know that you need a ufer ground, and a ground rod at the house, but this is a meter rack that is not attached to the house. It is in a field several yards away from the house.

I believe all of these items aren't necessary according to the code book. Am I correct?

You do not need rods at the house if you have a ufer (concrete encased electrode).
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Yes I figured that. I was just pointing it out it's location. When I first looked I did not see it either. He did a good job running the bare conductor. I was looking for the second.
 