AHJ seems to be making up his own code rules
I have never had to do this but why can't you leave the gec's as they are and just add another ground rod from the first rod
I'm curious how the OP connected the conductors from the 3 200 amp mains to the meter socket. I've only seen 320 meters accept 2 conductors.
That is a 600 amp meter base. The panel on the far right is feed out the back and there are 3 conductor lugs for it. There are CT's in the meterbase
You can see the pics in this thread. I did have to change the lugs to 3 conductor lugs. I had to order it thru the power company as the supply companies could get them. They gave me the lugs
I’ve got boxes of two hole and three hole spades we used to give away to electricians. Haven’t had anyone ask for them in a couple of years..
Think I may even have a few four hole spades.
Put them online I bet you can get a good price for them. I don't think I ever bought more than a couple of double lugs in my life.
He also said that I needed 2ea grounding rods (one on each end of the meter rack) instead of just one. I know that you need a ufer ground, and a ground rod at the house, but this is a meter rack that is not attached to the house. It is in a field several yards away from the house.
I believe all of these items aren't necessary according to the code book. Am I correct?
You do not need rods at the house if you have a ufer (concrete encased electrode).
Yes I figured that. I was just pointing it out it's location. When I first looked I did not see it either. He did a good job running the bare conductor. I was looking for the second.