I ICBJS New member Location Grand Rapids, MI Aug 22, 2008 #1 Can anyone here direct me to a chart or table that would show how to derate AIC ratings over distance based on conductor type?:-?
Can anyone here direct me to a chart or table that would show how to derate AIC ratings over distance based on conductor type?:-?
ron Senior Member Location New York, 40.7514,-73.9925 Aug 22, 2008 #2 You need to explain more details. AIC ratings do not get derated.
P Pete Benoit Member Location Western New York Aug 22, 2008 #3 I think what you are looking for can be found in the free stuff under fault current calculations
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Aug 22, 2008 #4 ron said: AIC ratings do not get derated. Click to expand... Ron is correct AIC ratings never change. What does change with distance is the available Short Circuit Amps (SCA).
ron said: AIC ratings do not get derated. Click to expand... Ron is correct AIC ratings never change. What does change with distance is the available Short Circuit Amps (SCA).