I asked for calculation of AIC rating per NEC 2014 section 110.9 and 110.10. The engineer coordinated with utility provided pdf from electric utility stating initial fault current are 22kA and these are subject to change anytime.
Engineer based calculation on this and showed AIC rating of equipment.
I sent comment back saying please provide worst case short circuit calculation utility xfmr impedance and size and infinite bus and that initial preliminary calculation is not acceptable and not in compliance 110.9 and 110.10.
I got response back saying they are in compliance.
Would the initial fault currents subject to change at the utility xfmr be acceptable or not? Would not one need wise case short circuit fault current based in poco xfmr impedance, size and infinite bus at primary?