AIC Ratings, and Available Fault Current at Service

Status
Not open for further replies.

bob

Senior Member
Location
Alabama
My predicament is, there are 18,332A in available fault current from the 75kw transformer that supplies this house (200A Service, 120/240 3W 1P). The transfer switch has a "Amps Withstanding" rating of only 10,000kA
THANKS!

Can you show us how you came up with the 18382 amps. I have an estimate of 12500 using a %Z of 2.5.
 

rcwilson

Senior Member
Location
Redmond, WA
Good point, Bob. Maybe the utility gave 18,332 amps as the 120V fault currrent.

If we use the assumption that the impedance on a single phase 240/120 V transformer feeding a 120V fault is about 20-50% higher than nameplate impedance, then 18.332 kA works out to a Z= 2.2%- 2.8 %. (Impedance on 120V is higher because only half of the secondary winding is in the circuit.)

18,332A x 120V = 2200 kVA short circuit.

75 kVA/ 2200 kVA = 3.4%

3.4% adjusted down for 20% = 3.4%/120%= 2.85%

3.4% adjusted down for 50% = 3.4%/150%= 2.23%

These numbers are more realistic.
 