My predicament is, there are 18,332A in available fault current from the 75kw transformer that supplies this house (200A Service, 120/240 3W 1P). The transfer switch has a "Amps Withstanding" rating of only 10,000kA
THANKS!
Can you show us how you came up with the 18382 amps. I have an estimate of 12500 using a %Z of 2.5.