celtic

Senior Member
Location
NJ
Is it permissible to have OCPDs with various AIC ratings within the same panel?

ie, 10k, 22k, 65k
 
celtic said:
Is it permissible to have OCPDs with various AIC ratings within the same panel?

ie, 10k, 22k, 65k

Yes

Most panels I have seen say that their UL Listed SCCR is equal to the AIC of lowest installed breaker.

In Square D I-Line panels the lowest AIC rating for 480V breakers is different for every frame size. For example, 18kAIC for a 100A FA, 25kAIC for a 200A KA, and 65kAIC for a 600A LC.
 