Most panels I have seen say that their UL Listed SCCR is equal to the AIC of lowest installed breaker.
In Square D I-Line panels the lowest AIC rating for 480V breakers is different for every frame size. For example, 18kAIC for a 100A FA, 25kAIC for a 200A KA, and 65kAIC for a 600A LC.