Installing a new 15HP 208 VAC 3-Phase Air Compressor.
Nameplate Amps: 42.7
Comp. has factory starter with O.L.'s.
Wire Size from local fused disconnect to compressor:
Per T. 430.250 wire size:
46.2 A x 125% = 57.75 Amps
So I would need #6 AWG XHHW. I will be installing XHHW wire.
Fuse Sizing:
Per T. 430.52 for Squirrel Cage Design B. I can size my local disconnect fuses at 175% of FLC for Dual Element Time Delay Fuses
46.2 x 175% = 80.8 Amp Time Delay Fuses. So 80A or 90A max. Fuses.
Breaker Sizing:
46.2 x 250% for Inverse Time Breaker feeding local fused disconnect = 115.5 Amp Breaker.
So if I install a 115 to 125 Amp (whatever I can purchase nearest to 115 Amps) circuit breaker How do I size the wire between the Breaker and the Local Fused Disconnect ?
Does the wire between the breaker and fused disco. need to be sized according to breaker size ?
Or does my interpretation of T 430.250 above also apply requiring me to run #6 AWG between the Breaker and Local Fused Disconnect ?
Nameplate Amps: 42.7
Comp. has factory starter with O.L.'s.
Wire Size from local fused disconnect to compressor:
Per T. 430.250 wire size:
46.2 A x 125% = 57.75 Amps
So I would need #6 AWG XHHW. I will be installing XHHW wire.
Fuse Sizing:
Per T. 430.52 for Squirrel Cage Design B. I can size my local disconnect fuses at 175% of FLC for Dual Element Time Delay Fuses
46.2 x 175% = 80.8 Amp Time Delay Fuses. So 80A or 90A max. Fuses.
Breaker Sizing:
46.2 x 250% for Inverse Time Breaker feeding local fused disconnect = 115.5 Amp Breaker.
So if I install a 115 to 125 Amp (whatever I can purchase nearest to 115 Amps) circuit breaker How do I size the wire between the Breaker and the Local Fused Disconnect ?
Does the wire between the breaker and fused disco. need to be sized according to breaker size ?
Or does my interpretation of T 430.250 above also apply requiring me to run #6 AWG between the Breaker and Local Fused Disconnect ?