Ok guys I need you to see if you can find any problems with this install. I do 99% resedential so I am a little unsure. I have a compressor to hook up
230 volt
7.5 hp
single phase
32 A
It is used and has a motor starter already on it it is a furnas (cat. no. 16cf15 alu). I plan to use no. 8 thhn (voltage drop is not a factor) and hook it to a 40A brkr.(32A * 1.25 = 40A) I will have a non fused disco. within sight.
sound good?
Does the motor starter have thermal protection in it? It does have a reset button on it. How do you know when you need a motor starter? Like I said it has a reset button on it does that take the place of the overloads ( heaters) Thanks for the help. Sorry for my ignorance. Any general htips for hooking up motors would be appreciated as far as the motor starter/ overloads go.
230 volt
7.5 hp
single phase
32 A
It is used and has a motor starter already on it it is a furnas (cat. no. 16cf15 alu). I plan to use no. 8 thhn (voltage drop is not a factor) and hook it to a 40A brkr.(32A * 1.25 = 40A) I will have a non fused disco. within sight.
sound good?
Does the motor starter have thermal protection in it? It does have a reset button on it. How do you know when you need a motor starter? Like I said it has a reset button on it does that take the place of the overloads ( heaters) Thanks for the help. Sorry for my ignorance. Any general htips for hooking up motors would be appreciated as far as the motor starter/ overloads go.