Having a debate,
A new replacement air compressor motor is rated at 20.3amps. Existing wiring is a 12 thhn on a 20amp breaker....can the 12 thhn be placed on a 25amp breaker? Or does the wiring also need to be upgraded to 10 thhn?
The breaker terminals are rated for 75°c, the pressure switch terminal ratings are unknown.
The ampacity chart rates 12 thhn for 25amps but then refers to 240.4(d) which then refers to 430 for motors.
Which method is acceptable?
Thanks!
Thanks!