220/221 said:
..In my head the electron flow in a short circuit BEFORE the motor would not go thru the overloads....hence the term "short" circuit.
Maybe this will help - I have often been asked a similar question about installations where a transformer secondary CB is 500 feet away from the transformer. Ususlly it starts out with:
What protects the secondary conductors from overcurrent?
The secondary CB. The current that goes into the transformer end on the conductors comes out of the cb end of the conductors.
But what if there is something wrong in the middle and the overcurrent doesn't come out the CB end of the conductors?
Ah - you're talking about a backhoe attack. In that case, you don't have any conductors to protect, they're toast. You just have a fire to put out. And the xfm primary will do that. Protecting against a conductor overcurrent in the middle on the run is not the job of a secondary CB. To protect against this failure mode, one uses concrete and steel.
This is similar to what you are discussing - an overcurrent/short circuit between the CB and the overload. You are dealing with a pick, hacksaw, forklift, .... Conductors are dead/gone. You just want the fire out.
A normal installation for me is a 40Hp, 480V, 3ph, FLA 49A, 3 - #6, OL set at 68A, CB set to 500A. (Listed combination starter with a mag only CB) Meets code and it's a good installation.
carl