mickeyrench
Senior Member
- Location
- edison, n.j.
i have a rtu that has a mca of 124 amps. with a mocp of 150 amps. i plan on using a cb rated for 150 amps. my conductors will be 2/0 only because the distance to the rtu is 130' and to be safe. we will use a 200 amp. non fused disconnect @ the unit. all in 2" conduit. this is a 3 phase 240 volt . if i missed something and i usally do can some one point it out before we get started.
thanks again.
thanks again.