mkgrady
Senior Member
- Location
- Massachusetts
I need to wire an air handler in a home that has built in emergency heat strips. The nameplate on the unit is wrong. It shows the MCA at 5 amps and 240 volts. It appears there are three 5KW strips so the real MCA would be over 60 amps without even counting the fan motor. Even the wiring diagram on the unit doesn't show any heat strips.
What has me stumped is the built in disconnects. There are two 60 amp 2 pole circuit breakers that feed the unit. Not sure why overcorrect protection is built in like that or why there are two breakers. I'm trying to anticipate how to wire the thing while I wait for the HVAC contractor to supply the real MCA and a wiring diagram. I doubt it needs two 60 amp circuits run to it but I really don't know what to expect. Can somebody take some mystery out of this for me?
What has me stumped is the built in disconnects. There are two 60 amp 2 pole circuit breakers that feed the unit. Not sure why overcorrect protection is built in like that or why there are two breakers. I'm trying to anticipate how to wire the thing while I wait for the HVAC contractor to supply the real MCA and a wiring diagram. I doubt it needs two 60 amp circuits run to it but I really don't know what to expect. Can somebody take some mystery out of this for me?