I agree.........the air handlers I see are part of a central heating/cooling system and I say each AH needs its own dedicated branch circuit.
Look at most # 6
I agree.........the air handlers I see are part of a central heating/cooling system and I say each AH needs its own dedicated branch circuit.
So this animal has no heat or a/c that it will be moving around. With except. #2 I believe that if this unit moved a/c it would qualify also. I know I will get arguments on that.
Look at most # 6
He said plain vanilla ,to me that means radiators.Ok....so we know there is a boiler as part of this system, therefore, this AH has hot water coils running thru it making it part of a central heating system.
He said plain vanilla ,to me that means radiators.
What i see out of the OP is he is looking at this already installed system to see if it complies with NEC and it does not.
Are a few easy ways to fix.
1 they could change disconnect switch at each unit to a 15 amp breaker and then the #12 on the 20 is a feeded. Unless it is having problems that is cheap way out.
2 run new circuits to 4 of them. That likely will cost far more.
One thing that bothers me is the unit is rated at 15 amp max breaker to protect the fan motor and 24 volt xformer. Had this been a 10 kw heat strip they would say 60 amp breaker. Most units do not have any other protection inside ,so that now has the fan motor on a 60 but thats ok. Why ?
I think Jim is saying that is this was a 10kw unit it would need a 60 amp breaker. When the a/c is on, the fan in the unit, which normally would require a 15 amp breaker, is now running on a 60 amp breaker.I have no idea at all what you are talking about here.
He said plain vanilla ,to me that means radiators.
I think Jim is saying that is this was a 10kw unit it would need a 60 amp breaker. When the a/c is on, the fan in the unit, which normally would require a 15 amp breaker, is now running on a 60 amp breaker.
Factory assembly. Like the fan motor on an AC compressor, if the motor needs additional protection, it's up to the manufacturer to include it.Most units do not have any other protection inside ,so that now has the fan motor on a 60 but thats ok. Why ?
Yes and he also said there is no protection for the motor and transformer which is untrue.
its part of a split unit for AC. Not always part of the heating system.So why have air handlers:-?
"Or they could simply leave it how it is."
Yes they can if they don't care about being in violation of NEC.
OK what protection does it have ? Very few have an extra fuse. Are you saying a 60 amp breaker protects a 3 amp fan motor ?
No I am saying the motor with have protection of some sort, impedance protected or internal thermal OL etc.
A class 2 transformer requires no protection.
its part of a split unit for AC. Not always part of the heating system.