looking at adding some lighting and general purpose recepts in a small privately owned hanger
i am reading 513.7(C) and i believe it is telling me explosion proof wiring methods
can i circumvent this requirement if i stay out of the locations that 513.3(C)1 and 513.7(C)?
 
looking at adding some lighting and general purpose recepts in a small privately owned hanger
i am reading 513.7(C) and i believe it is telling me explosion proof wiring methods
can i circumvent this requirement if i stay out of the locations that 513.3(C)1 and 513.7(C)?
(honestly just looking to see if i can use some 4square and industrial covers for recepts and switching if i stayed in a front corner of the hanger away from the 5' lateral rule and lighting more than 10' above the wings and engine)
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Arcing equipment, 10’ or less above classified locations, must be totally enclosed type or constructed so as to prevent the escape of sparks or hot metal particles - but not necessarily explosionproof.

Equipment in a classified area must be suitable for the location.
 