shouldnt we be using the 60 degree column for sizing 110.14(C)(1) (a) or do we know the terminals are rated 75 dergree then 110.14(C)(1)(a)(3) can be used..i have been told that all equiment is rated 75dergree terminals today...
If it is not NM or SE cable, you could use the column that the wire is listed for ampacity to start derating, but cannot exceed the ampacity of the temp limitation of the terminal.
310.15(B)
Tables. Ampacities for conductors rated 0 to 2000 volts shall be as specified in the Allowable Ampacity Table 310.15(B)(16) through Table 310.15(B)(19), and Ampacity Table 310.15(B)(20) and Table 310.15(B)(21) as modified by 310.15(B)(1) through (B)(7).
The temperature correction and adjustment factors shall be permitted to be applied to the ampacity for the temperature rating of the conductor, if the corrected and adjusted ampacity does not exceed the ampacity for the temperature rating of the termination in accordance with the provisions of 110.14(C).