Long run, may be well worth it.Anyone have any reasons not to use Aluminum wire for residential garage welder and compressor circuits?
Aluminum will probably not be available in smaller sizes you are likely to see in most residential garages but if it is, I see no reason not to use it.Anyone have any reasons not to use Aluminum wire for residential garage welder and compressor circuits?
What sized circuits?Anyone have any reasons not to use Aluminum wire for residential garage welder and compressor circuits?
Thank you I appreciate it.Long run, may be well worth it.
Compressor - presuming you are talking something that needs more than a 30 amp circuit. A lot of what goes into residential garage is no more than 20 amp. Until you get into some guy with serious air needs and he is maybe pushing the limit to what is allowed in some residential locations for regular activity.
35 & 50What sized circuits?
IDR if I've ever used SE cable.I generally don't use aluminum conductors smaller than 4 AWG. Might not really save much over copper if that is the size you run for say a 30 amp circuit - unless long length and voltage drop is a factor in conductor selection.
SE cable is about the only aluminum cable I have used, and that usually has always been 2 AWG or larger.
When still allowed to run 3 wire to ranges we almost always ran #6 copper SE cable to ranges.IDR if I've ever used SE cable.
We don't as a rule but we have some aluminium conductors. One was 40V, 40000A anodisors.I generally don't use aluminum conductors smaller than 4 AWG. Might not really save much over copper if that is the size you run for say a 30 amp circuit - unless long length and voltage drop is a factor in conductor selection.
SE cable is about the only aluminum cable I have used, and that usually has always been 2 AWG or larger.