Thanks for all the replies.
Sorry for the delay. Let me supply more info.
This is a simple transfer (throw-over) scheme that employs 2 MV vacuum breakers: Utility and Generator.
The logic is controlled by 2 Multilin relays: M60 and G60 (Main and Generator) and the SEL relay which I think is for redundant protection.
A power failure occurred, generator started, Main opened and Gen bkr closed.
Utility power returned, but instead of the Gen bkr opening and the Main bkr closing the Gen bkr stayed closed
and the LO alarm showed on the SEL and Failed To Transfer showed on the M60 and G60 relays.
I don't remember what I did to reset the alarms (this happened last year) but when I did, the Gen bkr immediately opened but the Main did not close. Found out later that the close spring charge circuit failed on the Main bkr (C-H VCP .) We manually charged the springs to get the Main bkr closed.
Our next step is to repair the charge circuit on the Main bkr or replace bkr with a spare that was just received.
Can someone answer how I was able to reset the alarms without accessing the program with a laptop.
To be quite honest, it’s hard to tell without the AcSELerator file. The logic can be programmed so many ways other than default.
Couple of things I noticed in your post..
The spring charge circuit isn’t in the logic? If the charge state has an IO point, it should be wired into the relay. That way you can put In logic so that the breaker won’t open without the charge spring being charged.
There is a reason the LO is a 1. Could the LO be tied to the 25 sync check also? Could have been this was a DTL event and the last time it happened it could have been some other type of event.
I would be more concerned over why the breaker opened last time when you hit reset. There should be some logic in there to make sure that doesn’t happen as it did.
Hook the laptop up. Pull a HIS, SER and an EVE from the terminal window. See what’s up with it...