Charles Sanford
Member
- Location
- Stockton CA, USA
Hello! I'm new to this Forum, but have been following it for several years.. I am rewiring my house, and I can't get the afci breakers to work. I have removed all the "state of the art" wiring from the 1940's to the newer stuff that others have patched in place. I kept the existing meter/main and replaced the main breaker. I jumpered from the neutral lug to the grounding lug at the main. I installed a new, Square D plug-in neutral bar panel with a floating neutral and grounds bonded to the panel. From that panel, I ran another sub-panel of the same type and configuration. And, when main is closed and power goes to the first and, then, to the second sub-panel, all the afci breakers are okay. However, when I place any load on any breaker, it trips. I replace some AFCI breakers with a older Bryant and Eaton breakers I had lying around, and they don't trip. The GFI receptacles hold and operate properly. The original, main breaker was corroded and the lugs were very small--I was stripping the screw head to tighten; so, I replaced the breaker thinking I had a loose or sloppy connection and consequent vibration... I thought I might have corrosion at the lugs on the neutral/ground bar; so, I jumped between the ground and neutral lugs with a bright #8 copper (it's only a 100 amp panel)... I tried the recommended test, and the breakers snap immediately, which indicates a grounded neutral or an arc fault?
Any recommendations?
Any recommendations?