green

Member
"RABBIT TAILS" , the home_insurance company asked if the outlets and such devices had rabbit tails . I have exhausted the knowledgeable I know and it has either been no reply or a simple miscommunication {refering to the copper pigtails added from device to line with what looks like antiox/shrink wrap} . thanks
 

bphgravity

Senior Member
Location
Florida
Re: ALL ALUMINUM RESIDENTIAL SYSTEM

The code does not allow the mixing of dissimilar metals, like copper and aluminum connections per Article 110.14. I do believe there are a few products on the market like "IDEAL 65 Twister Retrofits." I have also heard that there have been problems with these and other connectors especially with non-UL listed knock-offs.
The code does allow Al to be directly connected to devices if listed for use. See Articles 404.14(C) and 406.2(C) per specific requirements. :)
 