:thumbsup:I don't think so, Dennis. I think he has two MWBCs that have no connection to each other. Here is how he describes it:
For each of the two separate MWBCs, you have one neutral leaving the panel connecting to three neutrals leaving in three separate directions. The fact that the two wire nuts, each connecting the 4 white wires from its own MWBC, are installed in the same junction box does not change the (apparent - to me at least - but I still may be missing something) fact that the two MWBCs are independent of each other.
And as long as the wire nut is the point where a properly wired MWBC splits up in to three runs, each with one phase and a dedicated neutral, there would be nothing wrong with that setup.