Is anyone having issues with DC Buss Circuit issues on 753 PowerFlex VFD's?
We have a project where three out of 5 Allen Bradley Power Flex VFD's have failed, since startup in April. Last drive failure had 5 hours of operation on the drive.
L-L-L Voltage 490V. Tech support stating this is causing a high DC Buss Voltage near the trip level of the VFD. Recommends getting utility to lower incoming power as any voltage spikes will fault the VFD's.
New Siemens Surge suppression is not showing any voltage surges. Currently have a power quality analyzer installed trying to determine issue.
Any suggestions would be appreciated.
Thanks