mdshunk
Senior Member
- Location
- Right here.
I agree. It sounds like the OP is guessing at this point, which is a shame. I'd venture to say that 9 times out of 10 that I encounter problem that is neutral related, it's the POCO's problem. That's not to say that I don't end up having to troubleshoot their end anyhow to find it, but it's almost always a POCO problem Bad taps at the weatherhead, bad taps at the pole mount transformer, tree rubbed through aerial cable neutral, aerial neutral having a "missing section" for unclear reasons, underground cable having rotted out neutral, bad tap at padmount transformer flags, and a partly blown up primary to secondary netural jumper internal to the pole mount transformer are among the main reasons.e57 said:Hope you understand what I'm trying to say - you might look a little silly if after replacing the AL there is still a problem -
You can have an aerial tap that will visually look fine when you remove the cover. When you measure voltage on one conductor on one side if the tap, it'll be good. When you measure voltage on the other conductor on the other side of the tap, it'll be off. If you wrangle the tap around a bit, you can sometimes hear the tell-tale "sizzle" and maybe even get a few sparkles out of it.