I was called out to a house today that was victim of an electrical fire which happened in a finished room over a detached garage with the intent on checking the remaining system for safety. I found something that alarmed me, yet stumped me at the same time.
Single phase residential dwelling, 200 amp meter main combo servicing a 200 amp main breaker panel in the main house and 100 amp subpanel in the detached garage.
Garage breaker is locked out for the time being, for obvious reasons. The only load being passed thru to indoor panel and 2 breakers for a/c condensers.
Meter socket reads clean, 118v per leg. At the main breaker in the attached outdoor panel, I have the same voltage (with no load to indoor 200 amp panel). When I turn on the indoor panel voltages stay the same, but as I turn on certian breakers the voltages start acting really wierd. Prior to I had an even 118 per, and now it will jump to say 131 and 124, or 129 and 110...and so on and so fourth. There is no consistency to the fluctuation, but it always balances on the opposing circuit. Something keeps screaming neutral problem, but I can't think of what could possibly cause it.
One note I may add is it all has stayed within the + or - 10%, but having just had the fire, which started from "dirty power" (was metered at like roughly 145v over a 110 circuit) which blew up a tv/cable box.
Anyone ever experienced anything like this? Sorry to be so long winded but there was a lot going on in a small cottage on the beach.
Single phase residential dwelling, 200 amp meter main combo servicing a 200 amp main breaker panel in the main house and 100 amp subpanel in the detached garage.
Garage breaker is locked out for the time being, for obvious reasons. The only load being passed thru to indoor panel and 2 breakers for a/c condensers.
Meter socket reads clean, 118v per leg. At the main breaker in the attached outdoor panel, I have the same voltage (with no load to indoor 200 amp panel). When I turn on the indoor panel voltages stay the same, but as I turn on certian breakers the voltages start acting really wierd. Prior to I had an even 118 per, and now it will jump to say 131 and 124, or 129 and 110...and so on and so fourth. There is no consistency to the fluctuation, but it always balances on the opposing circuit. Something keeps screaming neutral problem, but I can't think of what could possibly cause it.
One note I may add is it all has stayed within the + or - 10%, but having just had the fire, which started from "dirty power" (was metered at like roughly 145v over a 110 circuit) which blew up a tv/cable box.
Anyone ever experienced anything like this? Sorry to be so long winded but there was a lot going on in a small cottage on the beach.