I was going to post this in the photovoltaic forum, but I think this is more of a general question:

Is there a less expensive, Code-compliant alternative to liquid-tight flexible metal conduit? For solar installs, those long DC optimizer output circuits that run through the attic can get expensive.

Thanks in advance.
 

Carultch

Senior Member
Location
Massachusetts
If it is in the attic, it is in a dry location, and the L in LFMC is no longer needed. FMC and EMT can be used instead. Metal Clad cable can also be an alternative.
 