fmtjfw
Senior Member
- Location
- Fairmont, WV, USA
Pardon my ignorance here, but is there actually a code section that requires the splices to be listed? I used to just use red or yellow wire nuts, and dip them in a can of Scotchcote.
110.14(B) Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically secure and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an identified insulation device.
Wire connectors or splicing means installed on conductors for direct burial shall be listed for such use.
Other provisions remove the insulation requirements for EGCs and prohibit soldering for same.