May look like USE cable, but doesn't appear to be marked as such.
Even if it is USE it can not be used indoors. There are conductors out there with multiple ratings marked on them - typically USE/RHW maybe with a -2 included. Those can be used both as direct bury and indoors (in a raceway).
My understanding is straight USE does not pass/ has not been tested for vertical flame and smoke producing characteristics and possibly some other things to allow it for use indoors.
:thumbsup:
If the OP wants to run it inside, even in a raceway it has to be a listed cable and have marking such as RHW, XHHW etc.