Oakey
Senior Member
- Location
- New Jersey
Ah yes 310.15 my bad. What is the breaker size for #2 for a sub feed?
Oakey said:Ah yes 310.15 my bad. What is the breaker size for #2 for a sub feed?
LarryFine said:No. #2 al may only be protected at 100a when it's the main feeder, not a sub-feeder.
Oakey said:I realize that 310.15(b)6 makes the rules for this size but pls bear with me here Im a little confused (doh!)..A #4 alum sub feed rated at 65 amps can be on a 70 breaker in the 75 column ...but a # 2 alum rated at 90 cannot be on a 100 breaker? Last question I promise LOL