aluminum feeder w/ copper ground?

Status
Not open for further replies.

malachi constant

Senior Member
Location
Minneapolis
I have a colleague (engineer) who would like to specify a copper equipment grounding conductor along with aluminum conductors, in the same raceway. Is there anything in the NEC that would prohibit this?
 
I agree with the others. You can have a copper equipment grounding conductor run with aluminum feeder conductors.

Chris
 