Cannot go bare with aluminum.
IMHO, single conductor bare aluminum will find few applications.
lizzie14 said:Is it ok to run aluminum phase conductors and a copper equipment ground? It has come up on a job and I've just never heard of that before.
wasasparky said:Not that anyone would do it, but are the three phase conductors required to be the same material?
raider1 said:No, as long as they are properly sized, there is no requirement for the different phase conductors to be the same material.
Now if you are paralleling conductors each conductor of the same phase must have the same conductor material. (See 310.4)
Chris
How about copper for half the run, then switch to aluminum? (assuming proper splicing method).
lizzie14 said:It goes from the utility transformer, to an exterior switchgear with main circuit breaker(this is the part I consider a feeder). Then it goes from the exterior switchgear to the main distribution panel which is the 3000A panel. From the SES (Service Exterior Switchgear) to the MDP, they have 8 sets of 4-750 kcmil Al and 1-400 kcmil Cu.