If a search is done, there will be many results on this topic, as I remember seeing it discussed quite a few times in the past. I was one who had responded to a few of the threads.
 
Years ago, I did a large (more than 10,000 splices) job with the Ideal Model 65 Twister wirenuts.
 
I have also been involved with the Tyco method installation, again 1000's of terminations.
 
Both have their plus an minus situations. 
 
I can tell you that the job I did with the Ideal wirenuts is still holding up well after more than 9 years. (one of my employees now holds a license and is doing maintenance in the buildings)
 
It all really boils down to proper installation, possibly being somewhat more careful and attentive towards aluminum installations. 
 
I will also say, that those buildings we performed the work on, 90% of the existing failures were on the grounded conductor, not the phase conductors, almost 99% were at the screw terminal of the devices, very, very few were at the wirenuts- which at the time were the plain old 'B' caps.