Aluminum Wiring

Status
Not open for further replies.

longrider

Member
Is there anything in the code book that states periodically maintenance of aluminum wiring ie: tightening lugs at the service panel and meter box?
 
peter d said:
No, not in the NEC.

It is NOT recomended that you re-tourqe a connections once it's made.

Not recommended by who ? I have gotten panels from the factory that the lugs were loose.
 
acrwc10 said:
I have gotten panels from the factory that the lugs were loose.

Having a loose factory lug is different that what we are talking about.

Once a wire is terminated into a mechanical lug and torqued correctly, it is not supposed to be re-torqued. It serves no purpose and may damage the conductor and/or the lug.
 
acrwc10 said:
Not recommended by who ? I have gotten panels from the factory that the lugs were loose.

In this situation the wiring has been pulled and terminated with aluminum wiring in a commerical building and what we need to determine how often the lugs need to be retorqued.
 
peter d said:
No, not in the NEC.

It is NOT recomended that you re-tourqe a connections once it's made.

In this situation the building has aluminum wiring. Are you stating that aluminum wiring does not need to be re-tourqe ?
 
longrider said:
Are you stating that aluminum wiring does not need to be re-tourqe ?

That is the case. Assuming they were installed properly, conductors should never be re-torqued.

Roger
 
roger said:
Assuming they were installed properly, conductors should never be re-torqued.
I'm sure most of you are referring to larger conductors, but if we're including residential-sized branch circuit conductors, I have to disagree. I've come across some very loose device terminals with aluminum wiring.

The problem is that cycling of current exacerbates the expansion/contraction snowballing that flattens the relatively soft wires under screw heads. The resistance creates more heat and more expansion.

Once flattened, re-tightening device screws added to the increased contact area can add years of useful life to aluminum-wired houses. The connections stay cooler and the wires stay tighter.
 
LarryFine said:
I'm sure most of you are referring to larger conductors, but if we're including residential-sized branch circuit conductors, I have to disagree. I've come across some very loose device terminals with aluminum wiring.

Once flattened, re-tightening device screws added to the increased contact area can add years of useful life to aluminum-wired houses. The connections stay cooler and the wires stay tighter.



Larry, do you know for a fact that those screw terminations were torqued from the beginning? I've come across loose AL connections also, but i'll bet you not one electrician from the 70's had a torque screwdriver...
 
longrider said:
Is there a section of the code that mentions about maintenance of aluminum wiring?

Being that you are an electrician and I assume somewhat familiar with the NEC, what section would you think it would be in?

Roger
 
90.2 Scope
(A) Covered This Code covers the installation of electrical conductors, equipment, and raceways; signaling and communications conductors, equipment, and raceways; and optical fiber cables and raceways for the following: ....
 
brian john said:


That was an interesting article,

Reliability Considerations
So, what about the residential Al branch wiring problems of the 1960s and 1970s? Solid Al wire sizes #12 and #10 AWG were used for branch-circuit-wiring in hundreds of thousands of homes in the late 1960s and early 1970s. In the U.S., the Consumer Product Safety Commission (CPSC) reacted to reports of overheating connections by conducting an investigation. Their research concluded that Al branch-circuit wiring connections were hazardous. This has a lot to do with the misperception that Al conductors in general are not as reliable as Cu.

Unbeknown to most is that the Canadian government conducted similar investigations, which concluded that, if properly installed, Al branch-circuit-wire connections are not hazardous. Furthermore, proposals to change the NEC to eliminate aluminum-branch-circuit wiring were rejected by the electrical experts on code-making panels and by UL.
 
stickboy1375 said:
Larry, do you know for a fact that those screw terminations were torqued from the beginning? I've come across loose AL connections also, but i'll bet you not one electrician from the 70's had a torque screwdriver...
Of course, I don't know that. One could claim that every loose connection was never correct. I also do not own a torque screwdriver, unless you count my experienced muscles.

I can only speak firsthand about my own troubleshooting experiences. I'm confidant that re-tightening aluminum terminations are preferable to not tightening loose ones.
 
LarryFine said:
I can only speak firsthand about my own troubleshooting experiences. I'm confidant that re-tightening aluminum terminations are preferable to not tightening loose ones.


I can agree 100% with that statement... But I would also say that goes with copper also...:grin:
 
LarryFine said:
Of course, I don't know that. One could claim that every loose connection was never correct. I also do not own a torque screwdriver, unless you count my experienced muscles.I can only speak firsthand about my own troubleshooting experiences. I'm confidant that re-tightening aluminum terminations are preferable to not tightening loose ones.


Ya right. I had a guy work for me once that didn't own a leval either he said " I have a leval eye" his work was Less then leval. :cool:
 
brian john said:
Great article brian,

I agree with most of what is mentioned with one major exception. When it comes to using a small solid Al conductor, it has heat cycling, corrosion degradation, and vibration prone 'qualities'. I have worked a few jobs repairing Al BC's and actually witnessed what an Al back-stabbed receptacle can do to a near-by couch or curtain. The flame-thrower that comes through the receptacle sockets are due to oxidation build-up that is ignited from plugging in a high current appliance and running about 12 amps, through the device. The spring clips have minimal contact 'faying surface' area that does not provide 'an effective bond', thus produces temperature cycling that creates more oxidization and conductor pitting until there is little left of the cross-sectional area to set the time-bomb off.
There were fatality counts in the 1970's that were attributed to the aluminum installation methods then that were NEC compliant as far as workmanship interpretations went. Instead of parallel pigtailing, series wiring through the device (that are still allowed) were the main flaw. So Al wiring got a bad rap because the product driven agenda didn't really agree with the determined reasons.

The newer Al alloy conductors exceed what was available then, but the same workmanship issue and allowed product usage is still ticking. I would not allow anyone to wire residential with #12, #10 and #8 solid conductor Aluminum because of the above reasons mentioned. Yes solid #8 sucks too. I have had to repair a few of those due to the heat degradation and inadequate conductor flexibility issues that cause fires. Now if we are talking 2008 AFCI protection, then that may just become nuisance callbacks. :) rbj
 
Last edited: