Bob, I can see multiple "Main Feeders" as follows.
(old post)
[FONT=Verdana, Helvetica, sans-serif]
[/FONT]
Roger[FONT=Verdana, Helvetica, sans-serif]
[/FONT]
(old post)
[FONT=Verdana, Helvetica, sans-serif]
[/FONT]
[FONT=Verdana, Helvetica, sans-serif]posted December 20, 2002 10:38 PM [/FONT][FONT=Verdana, Helvetica, sans-serif]
400A service 2-200 amp lighting appliance branch-circuit panels.
Service lateral --400KCM copper per article 310.15(b)(6) to 400A OCPD.
We still have not made it to our lighting appliance branch-circuit panels yet.
For sake of coversation we install 2-200 amp enclosed breakers adjacent to this 400 amp OCPD and feed these from parallel lugs. We use 2/0 copper per 310.15(b)(6).
We still have not made it to our lighting appliance branch-circuit panels yet.
We feed 2-200 amp lighting appliance branch-circuit panels with 2/0 copper per 310.15(b)(6)and make all terminations.
We have finally made it to our lighting appliance branch-circuit panels.
Now 310.15(b)(6) has seen it's end and if we feed any sub panel, say a 100 amp, from one of these aforementioned lighting appliance branch-circuit panels, this 100 amp sub panel can not use 310.15(b)(6)
[/FONT]
Roger[FONT=Verdana, Helvetica, sans-serif]
[/FONT]