It appears you got your wire dimensions from table 8... thats bare conductors.. for your THHN go back to Table 5, pg 678 ('08)
(I think your total will be .253 = over fill)
Well, who says they have to be insulated? If you can figure out a way to keep the wires from touching each other, the conduit, the boxes or the panel, what's the problem?Duh:roll: your right I was using bare conductor sizing. Thanks for the help.
The how about this one. The wire for a 10kW back up generator?
I=P/E
I=10,000/220
I=45.45amps
wire size #8awg thhn
You might find your 10kw generator has main lager than 40 amp... if so you would need to adjust your wire size for the OCP.
Then, IMO, a #8 (THWN) would be fine if your terminations are rated at 75? (110.14). In a NM or SE you would need a #6.