Inspector left me a correction notice on my Service Change out. "Ground needs to be #2 for this service" - 200 amp Service 4/0 alum going up my riser. i used a #4 solid copper armored for my ground to my ground rod. Am i reading 250.102(c)(1) Correctly? This is what I've done 100 times before and it's passed. Please Correct me if need be.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

You're both wrong; rods never require larger than #6 copper.

Read 250.66, including (A) and the Table.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We always use #6 stranded for the ground rod GEC. For #4/0 AL SEC's a #4 Cu GEC to the water pipe is the largest required so you would never need a #2 GEC for any electrode.
 