hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
Re: Am I required to replace this range circuit?
Fridjoc:
The reason for the change is the NEC does not allow for a SE cable to feed any appliance that uses the grounding conductor for a neutral and a ground even in an existing installation if this circuit is feed from a sub panel. I think the reason is there will be a voltage drop on the neutral bar in this sub-panel if the feeder run is long, this voltage drop will place a deferential voltage between the dryer/Range to anything that is bonded to the main service like the water pipes other appliances Etc...
Just a question are you getting SE cable crossed with FMC,BX or MC ?
[ December 11, 2003, 12:32 AM: Message edited by: hurk27 ]
Fridjoc:
If I'm getting this question right?why change the bare wire ( ground conductor) with the application of white tape to a "dedicated" neutral?
The reason for the change is the NEC does not allow for a SE cable to feed any appliance that uses the grounding conductor for a neutral and a ground even in an existing installation if this circuit is feed from a sub panel. I think the reason is there will be a voltage drop on the neutral bar in this sub-panel if the feeder run is long, this voltage drop will place a deferential voltage between the dryer/Range to anything that is bonded to the main service like the water pipes other appliances Etc...
If the concentric grounding conductor was not allowed to be used for over 20 amps then SE cable would not be allowed to be used for service entrance cable hence the name of the cable. and as a service cable the concentric neutral would have to be able to cary more than 20 amps.Presuming this range circiut is rated at greater than 20 amps and there by disqualifying the SE jacket as an acceptable ground conductor
Just a question are you getting SE cable crossed with FMC,BX or MC ?
[ December 11, 2003, 12:32 AM: Message edited by: hurk27 ]