amapacity of thermostat wire
realolman said:
Is there a problem with my wanting to know?
Nope, but most class 2 circuits are current limited so the ampacity of the cable is not an issue.
Right...., so the ampacity of 18. ga thermostat wire would be at least 5 a.?
and it doesn't matter if there are more than 3 current carrying conductors or not?
nakulak said:
although it doesn't apply (?), 725.23 has a clue.
Why wouldn't it apply?
725.3 Other Articles.
Circuits and equipment shall comply with the articles or sections listed in 725.3(A) through (G). Only those sections of Article 300 referenced in this article shall apply to Class 1, Class 2, and Class 3 circuits.
(A) Number and Size of Conductors in Raceway. Section 300.17.
300.17 Number and Size of Conductors in Raceway.
The number and size of conductors in any raceway shall not be more than will permit dissipation of the heat and ready installation or withdrawal of the conductors without damage to the conductors or to their insulation.
realolman said:
How can I find out or determine the ampacity of 18/3 and 18/5 thermostat wire?
even after you twist several of them together, I still don't think you're going to be able to run that receptacle off it.
:D
UL 508A has 16 gage at 10 amps and 18 gage at 7 amps.
There is a new article in the 2008 NEC on Amusement Park Rides it has ampacity of small conductors.
But T-stat cable does not have a voltage rating.
Sure it does: 300v.
From the Home Depot Worksite CD:
Thermostat and Bell Wire
"18-Gauge Thermostat Cable, Pacific Electricord"
"Rated to 105 degree Celsius. 300 Volts. CL-2. UL Listed."