Let's say I am going to feed an 800 amp switchboard through some existing conduits, which happen to be in a underground concrete ductbank for at least part of the run. The remaining feeder would be routed through ceiling cavities and chases of a healthcare facility. I would prefer to use two parallel sets of three hots and a ground; I have two spare 4" conduits available.
I would look at Table 310-16 and see that 600MCM's are good for 420 amps at 75C rating and 30C ambient temperature. At first glance, two sets of these would look to be okay. But if I have to derate them by a factor of even 0.94, they will be good for only 394.8A. And that's just for an increase of just one degree C.
How would I know how hot it's going to get inside the conduits in order to pick a temperature for derating the ampacity?
I would look at Table 310-16 and see that 600MCM's are good for 420 amps at 75C rating and 30C ambient temperature. At first glance, two sets of these would look to be okay. But if I have to derate them by a factor of even 0.94, they will be good for only 394.8A. And that's just for an increase of just one degree C.