I'm in the Phoenix area, so temperature derate for outdoor circuits is a must. As has been noted in other threads here the NEC is very ambiguous on what to use for ambient. The FPN in 310.15(B)(2)(c) suggest getting the "average ambient temperature" from ASHRAE Fundamentals. A couple of problems here. First, the text of the Code does not use the word "average". Second, ASHRAE Fundamentals lists an absolute maximum (which in the case of Phoenix is not the same as what the National Weather Service reports), and 2%, 1%, and 0.4% maximums.
I'm thinking that if the CMP chooses to be ambiguous then the design community needs to try to come up with a consensus on what to use for ambient so that we can have a "generally accepted standard" to cite when we're asked why we did the calculations as we did (especially if we have to defend a design in court or before a registration board).
My thoughts:
Using a 2% value (which means 2% of the hours in the year are above the temperature given) or a 1% or 0.4% value makes some sense for HVAC since it just means that the indoor temperature may be a tad higher than normal for a few hours. I'm not sure that that makes sense for electrical since it means we could be running the conductors above rated temperature.
On the other hand, using the maximum recorded temperature can raise costs significantly. Example: feeders to 200A residential panels in this area are generally #4/0 AL SER cable. With a 122 degF (highest recorded temperature) the derating is 205A X 0.82 = 168A and a 175A breaker must be used. With a 110 degF (ASHREA 2% temperature) the derate is 205A X 0.87 = 178A, and a 200A breaker can be used. The 400A "all in one" services that are generally used in this area come with a 200/2 main for the second panel. 175/2 breakers are not cheap.
Any and all comments are welcome.
Martin
I'm thinking that if the CMP chooses to be ambiguous then the design community needs to try to come up with a consensus on what to use for ambient so that we can have a "generally accepted standard" to cite when we're asked why we did the calculations as we did (especially if we have to defend a design in court or before a registration board).
My thoughts:
Using a 2% value (which means 2% of the hours in the year are above the temperature given) or a 1% or 0.4% value makes some sense for HVAC since it just means that the indoor temperature may be a tad higher than normal for a few hours. I'm not sure that that makes sense for electrical since it means we could be running the conductors above rated temperature.
On the other hand, using the maximum recorded temperature can raise costs significantly. Example: feeders to 200A residential panels in this area are generally #4/0 AL SER cable. With a 122 degF (highest recorded temperature) the derating is 205A X 0.82 = 168A and a 175A breaker must be used. With a 110 degF (ASHREA 2% temperature) the derate is 205A X 0.87 = 178A, and a 200A breaker can be used. The 400A "all in one" services that are generally used in this area come with a 200/2 main for the second panel. 175/2 breakers are not cheap.
Any and all comments are welcome.
Martin