jvacierto
- Van Wert, Ohio, USA
I work for an ambulance manufacturer, but I also have 5 years of experience in building electrical systems. Our customers connect their ambulances via cord-and-plug through a shoreline receptacle on the ambulance for battery charging and for power to 125V convenience outlets inside the ambulance. When the ambulance is NOT plugged in and the 125V are no powered, or they are power via an inverter or generator on the ambulance, I understand the 125V electrical system does NOT have to meet NEC, except as required by ambulance codes such as KKK and NFPA.
However, when the ambulance IS plugged in to the building, it is my belief the receptacles in the ambulance are then to be considered plugged into the building electrical system, and therefore the NEC would then have to be applied because of the cord-and-plug nature of the way the ambulance is being connected. Most of our customers use a 20A shoreline, therefore I treat the branch circuit as having a 20A breaker, meaning the 80% maximum amperage rule applies. I have been limiting our customer to having a maximum of 11 receptacles in the ambulance, but I am now getting push back. I have cited the sections in article 210 which show the correct load calculations for receptacles.