Question: NEC section 334.80 states that where more than two NM cables containing two or more current-carrying conductors are bundled together and pass through wood framing members that is to- be fire or draft stopped using thermal insulation or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a). Are the conductors considered bundled before going thru the framing member or bundled because they are going thru the framing member?
Panel Response: The bundled conductors are the conductors in the hole, which is not the point of this 334.80 code revision. The point of the revision is the fact that when too many conductors are run together (bundled) in a small space (hole) and then covered with fire- or draft-stopping material, this combination of events could create a hot spot in the conductors. See 334.80 that states, “Where more than two NM cables containing two or more current-carrying conductors are bundled together and pass through wood framing that is to be fire- or draft-stopped using thermal insulation or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).” In addition, NEC Code-Making Panel 7 has thus far accepted Proposal 7-72 for the 2008 NEC revision cycle that will remove the reference to bundled in Section 334.80.