amount of wires on a breaker

Status
Not open for further replies.

orelco1

Member
I understood that only one wire is alow to be installed on a circuit breaker.
I was reading on the Square D web site some 15,20 and 30 amps breakers are rating for two wires.
This means that a breaker can be use as an splice or two wire termination .

Please clarify,
Omar
 
Thats correct, all wire terminals are rated for a single conductor unless otherwise marked and listed.

Square D is just one breaker out of a few that is rated for two conductors.
 
iwire said:
Thats correct, all wire terminals are rated for a single conductor unless otherwise marked and listed.

Square D is just one breaker out of a few that is rated for two conductors.


one of the many reasons to go with square d :D

~Matt
 
It was working fine BEFORE you touched it

It was working fine BEFORE you touched it

That seems like a really bad idea.. leads to nothing but confusion. Anytime I open a panel, that is first thing I look for. You have to take the circuit breaker out of the panel to read the specs on the side. What happens if the breaker won't re-set or the bus bar has been arching for years. The customer is going to expect you to get the lights back on for free.
 
BLACK4TRUCK said:
That seems like a really bad idea.. leads to nothing but confusion. Anytime I open a panel, that is first thing I look for. You have to take the circuit breaker out of the panel to read the specs on the side. What happens if the breaker won't re-set or the bus bar has been arching for years. The customer is going to expect you to get the lights back on for free.

EVERYTHING works fine before it breaks down. This is where you need to educate the customer, not listen to them whine and complain.
 
BLACK4TRUCK said:
That seems like a really bad idea.. leads to nothing but confusion. Anytime I open a panel, that is first thing I look for. You have to take the circuit breaker out of the panel to read the specs on the side. What happens if the breaker won't re-set or the bus bar has been arching for years. The customer is going to expect you to get the lights back on for free.

Why would one or two conductors terminated per the listing make a difference?
 