Could someone please help me with this?
Last week at the plant we were testing out a used mixer powered by a 50HP 480v 3p motor and a VFD.
When it was running at full speed under no load the amp draw on all phases was less than 3 amps on the input of the VFD and 20+ on the output side phases.
I presume this is because the mixer was not under load. As the load increases the input amp draw should increase as well, correct?
It has been a while since I worked on such a large unit and was wondering if the readings sound normal or maybe there is a problem with the VFD.
The unit is older and documentation is somewhat unclear as it only states maximum specs. All of the parameters have been doublchecked to be correct.