I have recently ran into a problem with an A/C service tech. The problem is that an existing residential A/C condensor is starting to draw more current during the day and tripping the 2 pole 40 amp breaker. As I monitered the condensor with an Amp Probe the amps slowly started to rise as time went on. (a few hours) Eventually the breaker tripped. I figure the unit is just getting older and needs to be replaced. The A/C service tech's solution is to just put a 2 pole 50 amp breaker on the unit. (the unit is rated for 33 amp. minimum and 50 amp max fuse or circuit breaker) The problem is that the feeder for the unit is 8-2 RX cable. As I under stand it you can not exceed the 60 deg. C column for amperage on type NM-B cable. (which is 40 amps for #8 wire). The A/C service tech has told the Homeowner that because the unit is rated for 50 amp max, that is ok because it is A/C equipment and is not a problem. Is there am exception in the NEC that allowes for this change specifically for A/C equipment? If there is, I can't find it