Max Headroom
Senior Member
- Location
- Claremont CA 91711
- Occupation
- General Building Contractor/Electrical Contractor
I have a 40 amp circuit supplying a 7005w load (2 oven broiler elements in a otherwise gas range) I have run two 8ga cu(ungrounded conductors) and two 10ga ( neutral and EGC) in 3/4 EMT across a rooftop 1 1/2 " above the deck. Location is Upland CA, ambient temp as near as I can figure is 88F. I want to add two 12ga cu for a range-hood circuit and would like to pull them in with my 8 and 10 ga., I'm using THHN/THWN. It never rains during the hot months and if it did the temperature would be much cooler if that matters. If I adjust for the extra 2 conductors (0.8) and correct from Table 310.15 (B)(1) starting from the 75C column to 87-95F (0.94) I get 50A X .8X.94=38.4A. The breaker is a 2P 40A federal Pacific stab-lok assuming 60 degree (it's an old panel) the nema 14-50 R is rated 75 degree. I think I'm fine but would greatly appreciate your input. I think 240.4 (b), 210.19 a1b and 110.14C1a2 confirm that? Thank you for any feedback
