What they say, you'll have to derate. However, 9 switch legs, I assume it's a 20 or 30A circuit. In which case the derating starts at the wire ampacity, not the overcurrent protection. #12 is good for 30A, so even at 70% you still got 21A which is above the max overcurrent protection you can use. Now if the neutral is sharing, than it doesn't count so you're in the 70% derating (6-9). If that's not the case I believe you have to derate to the 60% (too lazy to check the code right now, but I'm pretty sure it's 60%) which only gives you 18A. It's abit beyond my understanding thought why you have 9 switch legs in a conduit, surely you don't have a 9 gang box? do you?