I don?t understand 392.11(A). It seems backwards.
I am contemplating using MC in tray as feeders to branch circuit panels. 392.11(A) says the ampacity is as shown in Table 310.16, as modified by (1) and (2) and (3).
? 392.11(A)(1) does not apply, as each feeder will have only 3 current carrying conductors.
? 392.11(A)(2) does not apply, as the tray will not be covered.
? 392.11(A)(3) tells me I have to use ?engineering supervision? ? that is, 310.15(C) ? to calculate the ampacity, but only if I keep ?one cable?s diameter? of separation between the cables. From my experience performing such ?under supervision? calculations, the answers are always, and I mean always, lower than the values in Table 310.16.
What if I do not keep that amount of separation between cables? What if I laid identical MC cables side-by-side in a single layer that goes the entire width of the tray? As I read it, that would mean that 392.11(A)(3) does not apply. That puts me back to 392.11(A), and I can then get ampacities directly from Table 310.16. Therefore, when I call for a configuration that clearly has more cables in closer proximity creating more heat, I get to use a higher ampacity that I would, if I spread them out.
What am I missing here?
I am contemplating using MC in tray as feeders to branch circuit panels. 392.11(A) says the ampacity is as shown in Table 310.16, as modified by (1) and (2) and (3).
? 392.11(A)(1) does not apply, as each feeder will have only 3 current carrying conductors.
? 392.11(A)(2) does not apply, as the tray will not be covered.
? 392.11(A)(3) tells me I have to use ?engineering supervision? ? that is, 310.15(C) ? to calculate the ampacity, but only if I keep ?one cable?s diameter? of separation between the cables. From my experience performing such ?under supervision? calculations, the answers are always, and I mean always, lower than the values in Table 310.16.
What if I do not keep that amount of separation between cables? What if I laid identical MC cables side-by-side in a single layer that goes the entire width of the tray? As I read it, that would mean that 392.11(A)(3) does not apply. That puts me back to 392.11(A), and I can then get ampacities directly from Table 310.16. Therefore, when I call for a configuration that clearly has more cables in closer proximity creating more heat, I get to use a higher ampacity that I would, if I spread them out.
What am I missing here?