- Location
- Massachusetts
Re: Ampacity of 12 THHN conductor
If the terminals, equipment and conductor insulation are all rated at least 75 C you may use the 75 C column meaning the 8 AWG THWN is rated 50 amps.
I ask you to point to a code section that says otherwise.
Bob
That is exactly what I am saying.Originally posted by james wuebker:
So you are saying if I use #8 THWN and the equipment is marked 75 C I can put a 50 breaker on this. I don't agree if this is what your saying.
If the terminals, equipment and conductor insulation are all rated at least 75 C you may use the 75 C column meaning the 8 AWG THWN is rated 50 amps.
I ask you to point to a code section that says otherwise.
Bob