See post #14. Branch ckt rating is ocpd size. Branch circuit rating 210.21(B)(2) says can be 15A or 20A while 240.4(B)(1) has to be 15A for cord and plug multi receptacles. What am I missing?
Sent from my SM-G935U using Tapatalk
What you are missing is that 240.21(B)(1) doesn't say that the ocpd size has to be 15A for cord and plug multi receptacle circuits. It doesn't say anything close to that.
See post #12.