philly

Senior Member
I'm looking at a cable spec sheet for 1/C 2kV extra flexible power cable that will be used in a temporary installation. The ampacity table gives the ampacity for the different cable sizes based on 40deg C ambient temperature or 90deg C conductor temperature.

Even though these cables are rated at 90deg C can you use this rating if they will be connected to lugs/equipment rated for 75 deg C? If not than how do you go about getting the 75deg value for the same cable if not published by manufacturer?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I just use the closest smaller size in Table 310.15(B)(16).

The 90°C rating can only be used for ampacity adjustment and or correction. The equipment, in almost all cases will limit you to the 75°C ampacities.

Note that to be used in an NEC application, the conductor insulation must be one of those listed in 310.104(A). Some flexible cables are dual listed to one of the types in the NEC and other flexible cables are not so listed.
 

brian john

Senior Member
Location
Leesburg, VA
Whats temporary? One day or 6 weeks?

For load test, we push 4/0 to 400 amps, for longer term temporary we are a tad more conservative than the tables
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
You don't mention stranding, but recognize that fine stranded cable (yeah, it may or may not be) requires suitable terminations. Temporary ... maybe you'll ignore that.
 

philly

Senior Member
I just use the closest smaller size in Table 310.15(B)(16). I'm not sure I follow your logic here. The particular cable that I am looking at is a 4/0 cable which on the cable datasheet it shows a 90deg rating of 405A. 310.15(B)(16) shows 4/0 as having 230A in the 75deg column and 260A in the 90 deg column.

How are you suggesting using the closest smaller size?

Whats temporary? One day or 6 weeks?

For load test, we push 4/0 to 400 amps, for longer term temporary we are a tad more conservative than the tables

This is for a project where utility power is down and it is unknown how long before it is back. So temporary in this case will be at least a few months but could be as long as a year before things are restored to normal.
 

Smart $

Esteemed Member
Location
Ohio
I just use the closest smaller size in Table 310.15(B)(16).
I'm not sure I follow your logic here. The particular cable that I am looking at is a 4/0 cable which on the cable datasheet it shows a 90deg rating of 405A. 310.15(B)(16) shows 4/0 as having 230A in the 75deg column and 260A in the 90 deg column.How are you suggesting using the closest smaller size?
There are several determinations to establishing a circuit rating. Don is referring to the one for terminal temperature limitations as stipulated in 110.14(C). He probably said the closest smaller size because he thought you had a flexible hard use cable with wire sized in mm², rather than one with AWG sizing.

As Code goes, the terminal temperature limitation for 4/0@75°C is 230A. To exceed this amperage is to say the terminal temperature would exceed 75°C. So as you can see, 230A caps the ampacity regardless of what its insulative properties will permit for the conditions of use in between terminals.

Here's a good, but dated paper on the matter: http://www2.schneider-electric.com/...2/en_US/Wire Terminations 0110DB9901R2-02.pdf
Note in particular Figure 9 and the text which describes its implementation.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
In my opinion, a good approximation it is according to IEEE 242/2001 ch. 9.5.2.2 Cable current and temperature:
TX = Ta + (TN – Ta) (IX / IN)2
where Tx=75oC Ta=40 TN=90 IN=rated ampacity at 90oC IX=rated ampacity at 75oC
Ix/In=sqrt((75-40)/(90-40))=0.866
For ambient correction factor see NEC [2014] 310.15 Ampacities for Conductors Rated 0–2000 Volts.
(B) Tables. (2) Ambient Temperature Correction Factors.
I’=SQRT((Tc-Ta’)/(Tc-Ta))
If Tc=75 Ta=40 and Ta’=30 then I’/I=SQRT((75-30)/(75-40))=1.134
So the new ampacity for Tc=75 and 30oC ambient is 0.98 of the previous.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
... He probably said the closest smaller size because he thought you had a flexible hard use cable with wire sized in mm², rather than one with AWG sizing. ...
Actually I was thinking of DLO that uses sizes like 262.6 and 313.3 kcmil. For those I would use the table values shown for 250 and 300 kcmil.
 

Smart $

Esteemed Member
Location
Ohio
Actually I was thinking of DLO that uses sizes like 262.6 and 313.3 kcmil. For those I would use the table values shown for 250 and 300 kcmil.
In any case, an NEC recognized cable type (not DLO, perhaps dual rated... RHW?) having an unrecognized size.
 